How to Build a Light Steel Structure Part 1
Printed From: FrameBuilder-MRD
Category: FrameBuilder MRD
Forum Name: DIY Advice
Forum Description: Ask for Help
URL: http://www.framebuilder-mrd.com/forum/forum_posts.asp?TID=90
Printed Date: 23 Nov 2024 at 6:15am Software Version: Web Wiz Forums 12.04 - http://www.webwizforums.com
Topic: How to Build a Light Steel Structure Part 1
Posted By: BSRSA
Subject: How to Build a Light Steel Structure Part 1
Date Posted: 24 Jan 2019 at 7:40am
Approach
These requirements are based primarily on the American Iron and Steel Institute’s (AISI) Specification for the Design of Cold-Formed Steel Structural Members
[1] for steel member
strength, on the American
Concrete Institutes’s (ACI) Building Code
Requirements for Structural Concrete
[2],
on the Structural Design of
Insulating Concrete
Form Walls
in Residential
Construction [3] for
concrete design and specification,
and on
the
Standard for Cold-Formed
Steel Framing -
Prescriptive Method for One and Two Family Dwellings
[29] for steel framing requirements. The provisions
for building
loads are based on the
American Society of Civil Engineers’
(ASCE) Minimum Design Loads for Buildings and Other Structures [4], the International Building Code [5], and the International Residential
Code [6].
These provisions
are intended
to represent
sound engineering and construction practice, taking
into account the need
for practical
and
affordable construction techniques
for
residential buildings. This document is
not intended
to restrict
the use of sound judgment or exact engineering analysis of specific applications.
Scope
The provisions
of this Prescriptive Method apply to the construction of detached
one- and two- family dwellings, townhouses, and other attached single-familydwellings in compliance with the general limitations of Table 2.1. The limitations are intended to define
the appropriate
use of
this document for most one-
and two-
family
dwellings. Using insulating concrete forms and cold-formed steel systems with other construction
materials in a single structure shall be
in accordance
with the applicable building code requirements for that material, the general limitations of Table 2.1, and
relevant
provisions of this document. An
engineered design shall be required for applications that do not meet the limitations
of Table 2.1.
The provisions
of the Prescriptive Method shall not apply to irregular structures or portions of structures in Seismic Design Categories C, D , and D . Only such irregular
portions of structures shall be designed in accordance with accepted engineering practice to the extent such irregular features
affect the performance of the structure. A portion of the building shall be considered
to be irregular when one or more of the following conditions occur:
- Exterior shear wall lines are not in one plane vertically from the foundation to the uppermost story in which they are required (i.e., cantilevers).
- A section of floor or roof is not laterally supported by shear walls on all edges.
- An opening in the floor or roof exceeds the lesser of 12 ft (3.7 m) or 50 percent of the least floor dimension.
- Portions of the floor are vertically offset.
- Shear walls (i.e. exterior ICF walls) do not occur in two perpendicular directions.
- Shear walls are constructed of dissimilar systems on any one story level.
TABLE 2.1
APPLICABILITY LIMITS
ATTRIBUTE
|
MAXIMUM LIMITATIONS
|
General
|
|
Building Dimensions
|
60 feet with center bearing wall or beam
32 feet without
center bearing wall or beam
|
Number of Stories
Design Wind Speed
|
2 stories above grade with a basement
130 mph (209 km/h) 3-second gust
|
Ground Snow Load
|
70 psf (3.4 kPa)
|
Seismic Design Category
|
A, B, C, D1 and D2 (Seismic Zones (0, 1, 2, 3, and
4)
|
Floors
|
|
Floor Dead
Load
|
10 psf (0.72
kPa)
|
First-Floor Live Load
|
40 psf (1.9 kPa)
|
Second-Floor Live Load
(sleeping rooms)
|
30 psf (1.4 kPa)
|
Floor Clear
Span (unsupported)
|
32 feet (9.8 m)
|
Walls - Concrete
Unit Weight of Concrete
|
150 pcf (23.6
kN/m3)
|
Wall Height
(unsupported)
|
10 feet (3 m)
|
Walls - Cold-Formed Steel
Wall Dead Load
|
10 psf (0.48
kN/m2)
|
Load Bearing Wall Height
|
10 feet (3 m)
|
Roofs
|
|
Roof and Ceiling Dead Load
|
15 psf (0.72
kPa)
|
Roof Live Load (ground snow load)
|
70 psf (3.4 kPa)
|
Roof Slope
|
3:12 to 12:12
|
Attic Live Load
|
20 psf (0.96
kPa)
|
Roof Clear Span (unsupported)
|
32 feet (9.8 m)
|
For SI: 1 foot = 0.3048 m; 1psf = 47.8804 Pa; 1 pcf = 157.0877 N/m3 = 16.0179 kg/m3; 1 mph =
1.6093 km/hr
|
Replies:
Posted By: BSRSA
Date Posted: 24 Jan 2019 at 7:45am
Definitions
The following
are definitions of key terms as they are used in this document. Figure
|
2.1 illustrates certain
terms as referenced
by these definitions.
|
Accepted Engineering Practice: An engineering approach that conforms with
accepted principles, tests, technical standards, and sound judgment.
|
Anchor Bolt:
A bolt, headed
or threaded, used to connect a structural member
of different material to a concrete member.
|
Approved: Reference to approval by the building code authority having jurisdiction.
A rational design by a competent
design professional shall constitute grounds for approval.
|
Attic: The enclosed
space between the ceiling joists of the top-most floor and the roof rafters
of a building
not intended for occupancy but sometimes used for storage.
|
Authority Having Jurisdiction: The organization, political subdivision, office, or individual charged with the responsibility of administering and enforcing
the provisions
of applicable building codes.
|
Axial Load: The longitudinal force acting
on a member. Examples are the gravity loads carried by columns or studs.
|
Backfill: The soil that is placed adjacent to completed portions of a below-grade structure (i.e., basement) with suitable compaction and allowance for settlement.
|
Basement: That portion
of a building, which is partly, or completely below grade
and which may be used as habitable space.
|
Bearing
Stiffener: Additional material that
is attached to the web to strengthen the member against web crippling. Also called a web stiffener.
|
Bond Beam: A continuous horizontal beam
of concrete with
steel reinforcement located in the exterior walls of a structure to tie the structure together and distribute
loads.
|
Buckling: A kink,
wrinkle, bulge, or otherwise loss of the original shape of a member due to compressive, bending, bearing, or shear loads.
|
Building:
Any one- or two-family dwelling or portion thereof that
is used for human habitation
Building Length: The dimension of a building that is perpendicular to roof rafters, roof trusses, or floor joists (L).
Building Width: The dimension of a building
that is parallel to roof rafters, roof trusses, or floor joists (W).
Ceiling Joist: A horizontal structural framing member that supports ceiling
components and which may be subject to attic loads.
C-Shape: A cold-formed steel shape used for structural and non-structural framing
members consisting
of a web, two (2) flanges and two (2) lips (edge stiffeners).
Clip Angle:
An L-shaped short piece of metal (normally with a 90-degree bend), typically used for connections.
Cold-Formed Sheet Steel:
A process where
light-gauge steel
members are manufactured by (1) press-braking blanks sheared from sheets or cut length of coils or
plates, or by (2) continuous roll forming of cold- or hot-rolled coils of sheet steel; both forming operations are performed at ambient
room temperature, that is, without
any addition of heat such as would be required
for hot forming.
Compressive Strength: The maximum ability of concrete to resist a compressive load, usually
measured in pounds per
square
inch
(psi) or Pascals
(Pa). The compressive strength
is based
on compression
tests of concrete cylinders that
are moist-cured for 28 days in accordance with ASTM
C 31 [7] and
ASTM C 39 [8].
Concrete Web: A concrete wall segment as per Figure 2.1, a minimum of 2 inches
(51 mm) thick, connecting
the vertical and horizontal concrete members (cores) of a
waffle-grid ICF
wall
or lintel
member. Webs may contain
form ties but are
not reinforced (i.e., vertical or horizontal reinforcement or stirrups).
Crawlspace: A type of building
foundation that uses a perimeter
foundation wall to create an under floor space which is not habitable.
Dead Load: Forces resulting
from the weight of walls,
partitions, framing,
floors, ceilings, roofs, and
all other
permanent construction entering into,
and becoming
part of, a building.
Deflection: Elastic movement
of a loaded structural
member or assembly (i.e.,
beam or wall).
|
|
Posted By: BSRSA
Date Posted: 24 Jan 2019 at 7:47am
Design Professional: An individual who is registered or licensed
to practice their
respective design
profession as defined by the statutory requirements of the state
in which the project is to be constructed.
|
Design (or Basic) Wind Speed: Related to winds
that are expected
to be exceeded
once every 50 years at a given site (i.e., 50-year return period). Wind speeds in this
document are given in units
of miles per hour (mph) by 3-second gust measurements
in accordance with ASCE 7 [4].
|
Dwelling: Any building that contains one or two dwelling units for living purposes.
|
Edge Stiffener: The part of a C-shape
framing member that extends from the flange as a stiffening element that extends perpendicular to the flange.
|
Endwall: The exterior wall of a building which is
perpendicular to the
roof ridge and parallel to
floor framing,
roof rafters,
or
trusses. It is normally the
shorter dimension of a rectangular building’s footprint.
|
Exposure Categories: Reflects the effect of the ground surface roughness on wind loads in accordance with ASCE 7 [4]. Exposure Category B includes
urban and suburban areas, or other terrain with numerous closely spaced obstructions having
the size of single-family dwellings or larger.
Exposure Category C includes open terrain with scattered
obstructions having heights generally less than 30 ft (9.1 m) and shorelines
in
hurricane prone regions. Exposure D includes
open exposure to large
bodies of water in non-hurricane-prone regions.
|
Flange: The portion
of the C-shape
framing member or track that is perpendicular
to the web.
|
Flat Wall: A solid concrete
wall of uniform thickness produced by ICFs or other
forming systems.
|
Floor Joist: A horizontal structural framing member that supports floor loads and
superimposed vertical loads.
|
Form Tie: The element of an ICF
system that holds
both sides of the form
together. Form ties can be steel, solid plastic, foam plastic,
a composite of cement
and wood chips, a composite of cement and foam plastic, or other suitable material capable of resisting the loads created by wet concrete. Form ties
remain permanently embedded
in the concrete wall.
|
Foundation: The structural elements through which the load of a structure is transmitted to the earth.
|
|
Posted By: BSRSA
Date Posted: 24 Jan 2019 at 7:48am
Foundation Wall: The structural element of a foundation
that transmits the load of a structure to the earth; includes basement, stem, and crawlspace walls.
Grade: The finished ground level adjoining the building at all exterior walls.
Ground Snow Load:
Measured load on the ground due to snow accumulation
developed from a
statistical analysis of
weather records expected
to be exceeded once every 50 years at a given site.
Horizontal Reinforcement: Steel reinforcement
placed horizontally in concrete walls to
provide resistance to
temperature and shrinkage
cracking.
In certain circumstances, horizontal reinforcement is required for additional strength around openings
and in
high loading conditions such as
experienced in hurricanes and earthquakes.
In-Line Framing: A framing method
where all vertical and horizontal load carrying members are aligned.
Insulating Concrete Forms (ICFs):
A concrete forming system using stay-in-
place forms of foam plastic insulation, a composite
of cement and foam insulation,
a composite of cement and wood chips, or other insulating
material for constructing cast-in-place concrete walls. Some systems
are designed
to have one or both faces of the form removed after construction.
J Bolt: A threaded anchor bolt typically
embedded in concrete with threads on one end and a crook in the shank at the other; used to connect a structural member of different material to a concrete member.
Lateral Load: A horizontal force, created by wind or earthquake, acting on a
structure or its components.
Lateral Support: A horizontal member providing stability
to a column or wall across its smallest dimension.
Ledger: A horizontal structural member fastened to a wall to serve as a connection
point for other structural members,
typically floor joists.
Lip: See edge stiffener.
Live Load: Any gravity load that is not permanently applied to a structure; typically
transient and
sustained gravity
forces resulting
from
the weight
of people
and furnishings, respectively.
|
Posted By: BSRSA
Date Posted: 24 Jan 2019 at 7:49am
Material Thickness (Steel): The base metal thickness excluding any protective
coatings. Thickness is now commonly expressed in mils (1/1000 of an inch).
|
Metallic Coated Steel:
Steel that has a metallic
coating for protection against corrosion. The level of protection provided is measured by the weight of the metallic coating applied to
the surface area of
the steel. Typical
metallic coatings are galvanizing,
galvalume, or galfan, which are zinc-based.
|
Mil: A unit of measurement equal
to 1/1000 of an inch (e.g., 33 mil = 0.033 inch).
|
Multiple Span: The span made by a continuous member having intermediate
supports.
|
Non-Structural Walls: Refer to walls.
|
Post-and-Beam Wall: A perforated concrete
wall with widely spaced (greater than that required for screen-grid
walls) vertical and
horizontal concrete members
(cores) with voids in the concrete between
the cores created by the ICF form (i.e., flat, waffle-, or screen-grid as per Figure 2.1).
|
Ridge: The horizontal line formed by the joining
of the top edges of two sloping
roof surfaces.
|
Roof Snow Load:
Uniform live load
on the roof due to snow accumulation; roughly equivalent
to 70 to 80 percent of the ground snow load in accordance with ASCE 7 [4].
|
Screen-Grid Wall: A perforated concrete
wall with closely spaced vertical
and horizontal
concrete members (cores) with voids
in the concrete between the members
created by the ICF form as per Figure 2.1. It is also called
an interrupted-grid wall or post-and-beam
wall in other publications.
|
Seismic Load:
The force exerted on a building
structure resulting from seismic
(earthquake) ground
motions.
|
Seismic Design Categories: Designated seismic hazard
levels associated with a particular
level or
range
of seismic risk and
associated seismic design
parameters (i.e., spectral response
acceleration and building importance).
Seismic Design Categories A, B,
C,
D1, and D2 (Seismic
Zones
0,
1, 2, 3, and 4)
correspond to successively greater seismic design loads; refer to the IBC [5] and IRC [6].
|
Sill Plate: A horizontal member
constructed of wood, steel, or other suitable material that is fastened to the top of a concrete
wall, providing a suitable surface for fastening structural members constructed of different materials
to the concrete wall.
|
|
Posted By: BSRSA
Date Posted: 24 Jan 2019 at 7:50am
Slab-on-Grade: A concrete
floor, which is supported
by, or rests on, the soil directly below.
Slump: A measure of consistency of freshly mixed
concrete equal to the amount that a cone of uncured concrete
sags below the mold height after the cone-shaped
mold is removed in accordance with ASTM C 143 [9].
Smoke-Development Rating: The combustibility
of a material that contributes to fire impact through
life hazard
and property
damage by producing smoke and toxic
gases; refer to
ASTM E 84 [10].
Span: The clear horizontal
distance between bearing supports.
Stem Wall: A below-grade foundation
wall
supported directly by the soil
or on
a footing. Wall thickness and
height are determined as that
which can adequately distribute the building loads safely to the earth.
Stirrup: Steel bars, wires, or welded wire fabric located
perpendicular to horizontal reinforcement and extending
across the depth of the
member in concrete beams,
lintels, or similar members subject to large shear loads.
Story: That portion of the building included between the upper surface of any floor and
the upper surface of the floor next above, except that the top-most story shall
be that habitable
portion of a building
included between the upper surface of
the top-most floor and the ceiling or roof above.
Story Above-Grade: Any story with its finished
floor surface entirely above grade except that a basement
shall be considered as a story above-grade when the finished surface
of the
floor above the basement is
(a) more than
6 feet (1.8 m) above
the grade plane, (b) more than 6 feet (1.8 m) above the finished
ground level for more
than 50 percent of
the total
building perimeter, or
(c) more
than 12 feet (3.7 m)
above the finished ground level at any point.
Strap: Flat or coiled
sheet steel material typically
used for bracing and
blocking which transfers
loads by tension and/or shear.
Stud: Vertical structural element of a wall assembly, which supports
vertical loads
and/or transfers
lateral loads.
Townhouse: Attached single-family dwelling units constructed in a row with each unit separated by fire walls at property lines.
|
Posted By: BSRSA
Date Posted: 24 Jan 2019 at 7:57am
Track: A framing
member consisting of only a web
and two
(2) flanges.
Track depth
measurements are taken to the inside of the flanges.
Truss: A coplanar system of
structural members joined
together at their ends usually to construct a series of triangles
that form a stable beam-like framework.
Vertical Reinforcement: Steel reinforcement placed
vertically in concrete walls
to strengthen
the wall
against lateral forces
and eccentric
loads. In certain circumstances, vertical
reinforcement is required for additional
strength around openings.
Waffle-Grid
Wall: A solid concrete
wall with closely spaced vertical and horizontal
concrete members
(cores) with a concrete web between the members created
by the ICF form; refer to Figure 2.1. The thicker vertical and horizontal concrete
cores and the thinner concrete webs create the appearance of a breakfast waffle. It is also referred to as an uninterrupted-grid wall in other publications.
Wall Height: The clear vertical distance
between the finished
floor and the finished
ceiling. Where a finished floor does not exist (i.e., crawlspace),
the wall height is the
clear vertical distance between the interior finish grade and the finished ceiling.
Walls (steel):
Structural or Load
Bearing:
Wall systems
subject to loads
that exceed the limits for a non-structural system.
Non-Structural or Non-Load
Bearing: Wall systems that
are limited
to a lateral (transverse)
load of not more
than 5 psf (240 Pa),
a superimposed vertical
load per member, exclusive of sheathing materials, of not more than
100 lb/ft (1460
N/m), or a
superimposed vertical
load
per member of not
more than 200 lbs (890 N).
Web: That portion of a framing member that connects the flanges.
Web Crippling: The localized permanent (inelastic) deformation of the web member
subjected to concentrated load or reaction at bearing supports.
Web Stiffener: Additional material
that
is attached to the web to strengthen the
member against
web crippling. Also called a bearing stiffener.
Wind
Exposure: refer to Exposure Categories.
|
Posted By: BSRSA
Date Posted: 24 Jan 2019 at 7:57am
Wind Load: The force or pressure exerted on a building
structure and its components
resulting from wind.
Wind loads are typically
measured in pounds
per square foot (psf) or Pascals
(Pa).
Wind Speed: Wind speed is the design wind speed related
to winds that are expected
to be exceeded
once every 50
years at a given
site (i.e., 50
year-return period).
Wind speeds in this
document are given in units
of miles
per hour
(mph) by “3- second
gust†measurements (refer to Table 2.2 to convert to fastest-mile wind speed).
TABLE 2.2
EQUIVALENT BASIC WIND SPEEDS
(mph)1
Fastest Mile
|
70
|
75
|
80
|
85
|
90
|
100
|
110
|
3-Second Gust
|
85
|
90
|
100
|
105
|
110
|
120
|
130
|
For SI: 1 mph = 1.609 km/hr = 0.447 m/sec
1 Linear interpolation is permitted.
Yield Strength: A characteristic of the basic strength of the steel material defined
as the highest unit stress that the material can endure before permanent deformation
occurs as measured by a tensile test in accordance
with ASTM A 370 [11].
|
|